Communicating with Siemens LOGO! 8.

This article illustrates how to establish communication between Elipse E3 and Siemens's LOGO! 8 PLC. To do so, we'll use Siemens M-Prot driver for communicating via Ethernet, and also the vendor's software, LOGO Comfort, to develop the structure to be accessed by the driver.

Device's addressing:



Digital input (I): 8 bytes, starting at DB1:DBB1024
Digital output (Q): 32 bytes, starting at DB1:DBB1064
Analog input (AI): 8 bytes, starting at DB1:DBW1032
Analog output (AQ): 32 bytes, starting at DB1:DBW1072
Digital flag (M): 14 bytes, starting at DB1:DBW1104
Analog flag (AM): 128 bytes, starting at DB1:DBW1118
Network input (NI): 16 bytes, starting at DB1:DBW1246
Network analog Input (NAI): 128 bytes, starting at DB1:DBW1262
Network output (NQ): 16 bytes, starting at DB1:DBW1390
Network analog output (NAQ): 64 bytes, starting at DB1:DBW1406

Structure developed at Logo Comfort
*Demo attached CircuitDiagram1.lsc




Siemens M-Prot driver settings:

After compiling and recording the program in the PLC, we'll set up the supervisory. Add the M-Prot driver to the project and fill in the following settings:

M-Prot tab:  

    Network: ISOTCP
    Use Dest. TSAP: active
    Dest. TSAP (hex): 002 (or any value between the range accepted by the PLC)




Setup tab:
    Physical Layer: Ethernet

Ethernet tab:
    Main IP: device's IP
    Port: port used for communication purposes




Tags parameterization:

Settings with Syntactic Parameters (Item) and settings with Numerical Parameters (N/B):

NOTE: To check the information on Datatype and Area as seen below, please refer to Siemens M-Prot driver's manual (Tag Reference tab).

When configuring the device with Syntactic Parameters, add the network device address to the driver's Device field. At Item device, follow the syntax below for a DB-type area:

DB<NumberDB>:<Type><Address><[.Bit]>

For example, for a Word added to a DB at 1032 address:

Device = 0
Item = DB1:DBW1032

When configuring with Numerical Parameters (N/B):

N1/B1 = PLC address
N2/B2 = DataType × 100 + Area
N3/B3 = 0
N4/B4 = are address

For example, a Word added to a DB at 1032 address would be:

N1/B1 = 0
N2/B2 = 309
N3/B3 = 0
N4/B4 = 1032





Attached demo application:



Device used for testing purposes:


 
Salvar


Artigos Relacionados

Este artigo não possui outros artigos relacionados.

Anexos

Comentários de Usuários

Nenhum comentário de usuário. Adicionar um comentário

Comentários do artigo 'Communicating with Siemens LOGO! 8.'

Para adicionar um comentário neste artigo, preencha os campos abaixo. Os campos marcados com asterisco são obrigatórios.

   Nome:
   E-mail:
* Comentário:
* Digite o código abaixo:

 

Detalhes do Artigo

Última Atualização
11th of October, 2017

Autor
Vinícius Dalla Vecchia

Você gostaria de...

Imprimir esta página  Imprimir esta página

Enviar por e-mail esta página  Enviar por e-mail esta página

Adicionar um comentário  Adicionar um comentário

 Avise-me

Avise-me  Adicionar aos favoritos

Remover Marcação Remover Marcação

Editar este Artigo

Edição Rápida


Opinião dos Usuários

Nenhum usuário votou ainda.

Como você classifica este artigo?




Obrigado pelo seu voto.

Continuar